Thermal Blocks-HVAC Zones designed
NC-2009 EAp2:Minimum energy performanceposted by Elena Grau on
Hello, I'm working in the simulation of a building which has many HVAC zones defined so that should be modeled each ones as a separated thermical block but the zones of proposed building complies t
Selecting system type
NC-2009 EAp2:Minimum energy performanceposted by Haojie Wang on
We have a project that consists of both residential and non residential units. Per 90.1 2007G3.1.1 exception a. we need to use two HVAC system types for residential and non-residential separately.
California Projects using Title 24-2013
NC-2009 EAp2:Minimum energy performanceposted by Cindy Quinn on
To comply with California codes we had to show compliance with Title 24-2013. This required us to use the proprietary program Energy Pro 6.
How to model the ventilation system for baseline model.
NC-2009 EAp2:Minimum energy performanceposted by La Verne Ramir Certeza on
Hello, I would just like to ask regarding how I should model the ventilation system of my baseline model. My project is a hotel building which uses chilled water as its main cooling medium.
Using Desiccant Dehumidification - What about the Baseline?
NC-2009 EAp2:Minimum energy performanceposted by Mark Benson on
In some cases, such as Hospital operating rooms and Ice Rinks, you have to maintain indoor air dewpoint temperaturs lower than 44 F.
All electric Residential Building
NC-2009 EAp2:Minimum energy performanceposted by Emmanuel Pauwels on
Hi, we are working on a residential project.
Baseline service water heater
NC-2009 EAp2:Minimum energy performanceposted by Mark Benson on
In the proposed design, we are using a water-to-water heat pump for the sole purpose of service water heating. Voltage and Amps are 460v and 140 RLA, respectively.
Natural Ventilation in Baseline?
NC-2009 EAp2:Minimum energy performanceposted by Marina Andrade on
In environments where they will be covered by natural ventilation, how should I proceed in baseline model? For example, a factory or warehouse with the proposed natural ventilation, must be equal
VAV minimum flow set points
NC-2009 EAp2:Minimum energy performanceposted by Victoria Watson on
Hi, Appendix G3.1.3.13 says "Minimum volume setpoints for VAV reheat boxes shall be 2.15 L/s·m2 of floor area served or the minimum ventilation rate, whichever is larger" When you have a HVAC sys